Good question, it seems there is noting specific to this in the codebook. When I was in Alberta I called the AHJ with this same question and I never did get a definitive answer.
Hopefully someone has an answer.
I am wondering what the minninum distance is between a hot tub and a w/p resedential meter socket?
Good question, it seems there is noting specific to this in the codebook. When I was in Alberta I called the AHJ with this same question and I never did get a definitive answer.
Hopefully someone has an answer.
It has to be at least 3M away unless separated by a fence, wall, or other permanent barrier.
68-068 (7) Except as permitted by Rule 68-070, the following equipment shall be protected by a ground fault circuit interrupter:
(a) Electrical equipment placed in the water in the pool; and
(b) Audio amplifiers connected to loudspeakers in the pool water; and
(c) Electrical equipment located within the confines of the pool walls or within 3 m of the inside walls of the pool and not suitably separated from the pool area by a fence, wall, or other permanent barrier; and
(d) Receptacles located in wet areas of a building, and associated with the pool, such as locker and change rooms.
<font size="2" face="Verdana, Helvetica, sans-serif">My question to the AHJ was does the conduit and the WP meter constitute a suitably permanent barrier, I never did receive an answer and I do suspect it does not, but I was hoping for a solid answer(c) Electrical equipment located within the confines of the pool walls or within 3 m of the inside walls of the pool and not suitably separated from the pool area by a fence, wall, or <font color="red">other permanent barrier;</font>